Quick answer
Not necessarily. Under the Energy Networks Association rules G98 covers generating units up to 16 A per phase (3.68 kW on a single-phase supply, 11.04 kW on three-phase); larger systems need a G99 application approved before work starts, and the network operator may set an export limit. Whether a church needs three-phase depends on system size, the existing supply and any heat pump or EV charging planned.
Full answer
UK electricity supply standards: single-phase 230V is standard for domestic and small-commercial properties. Three-phase 400V is standard for commercial premises with larger demand. Most parish churches have legacy single-phase supplies.
Solar PV connection rules (Energy Networks Association G98 and G99 standards): G98 is the notification route for generating units up to 16 A per phase: 3.68 kW on a single-phase supply and 11.04 kW across three phases. Above that, a G99 application must be approved before work starts.
For a system above 3.68 kW on a single-phase supply, ask the network operator what it will accept and whether an export limit or a three-phase upgrade is needed.
Three-phase upgrade costs are set by the network operator and an electrician, so get a written quote. It is worth considering if a larger system, a heat pump or EV charging is planned.